Hi all , 

I'm currently using the EVSPIN32G4 evaluation board along with MC Workbench for motor control development, and I'm encountering an issue with Overcurrent Protection (OCP) behavior that I can’t quite resolve.

My Setup:
Gain Type: External Gain Net
OCP Threshold (set in MC Workbench): 200A
Shunt Resistor: Physically modified to 1mΩ (0.001Ω)
External Amplifier Gain: 7.33

1746582341903.jpg

1746582329251.jpg

During runtime, I monitored the motor phase current using a current probe and oscilloscope. OCP is triggered at only around 46A, which is far below the configured 200A.

In the firmware, I noticed:

DAC_OCP_Threshold = 7427;

According to the MC SDK, the current conversion factor is calculated using this formula:

#define CURRENT_CONV_FACTOR ((uint16_t)((65536.0 * RSHUNT * GAIN) / ADC_REFERENCE_VOLTAGE))

I get: CURRENT_CONV_FACTOR ≈ 146 ///   I = 7427/146 = 50.9A

In the official ST document UM2850 - Getting Started with EVSPIN32G4, Section 5.5.2 provides a OCP threshold formula.

1746583672261.jpg

The formula is used to calculate the actual overcurrent protection (OCP) trigger current based on the hardware resistor network.

I’m unsure whether this discrepancy is due to a misunderstanding on my side, or if there’s a misconfiguration in the setup.I hope someone can help me clarify this issue.

Thanks

1 reply

GMA
ST Technical Moderator
May 20, 2025

Hello @1123,

How did you measure the 46A current value? The most accurate is to measure with a scope the voltage at Rshunt point.
Signal could be noisy; could you try by increasing the Digital Filter Duration?

GMA_0-1747754916201.png

 

If you agree with the answer, please accept it by clicking on 'Best answer'.Best regards.GMA