How can we use RS-485 in full-duplex ?

ranran
Senior II

Hello,

We need to use RS-485 in full duplex, and with the flow control (DE).

Is it that when we configure DE with RS485 is shall be used as half duplex ?

can I configure rs232 pins with RTS (instead of DE) before converting voltage to rs-485 levels ?

Will this create a full duplex connection ? (CTS shall always be active in order to provide full duplex connection)

Thank you,

ran

1 ACCEPTED SOLUTION

Accepted Solutions

A differential driver has two wires (a pair) coming out of it.

If you are doing

TX -> RX

RX <-TX

RTS -> CTS

That's THREE PAIRS using differential drivers.

You and the HW guys need to have a clear understanding of what it is you are doing, and what full and half-duplex mean, you seem confused about pretty basic concepts here.

Tips, Buy me a coffee, or three.. PayPal Venmo
Up vote any posts that you find helpful, it shows what's working..

View solution in original post

16 REPLIES 16

>>We need to use RS-485 in full duplex...

That might prove quite challenging given the nature of the connection. Perhaps you're thinking of RS-422?

Tips, Buy me a coffee, or three.. PayPal Venmo
Up vote any posts that you find helpful, it shows what's working..
ranran
Senior II

The HW engineer says it is a matter of voltage levels for the rs485.

He says that the devices in the end are capable of full duplex.

Hi,

Our HW engineer need the voltage levels of rs485.

Maybe we can configure the USART to use only RTS (instead of DE).

As I see flow control options are capable to use both RTS_CTS or only one of them (RTS or CTS alone) .

With this configuration I assume that the controller will remain in full duplex, Right ?

Thank you,

ran

Do you actually need hardware flow control in your application?

Look up diagrams of an RS-422 interface, ie where each signal is passed as a differential pair.​

Tips, Buy me a coffee, or three.. PayPal Venmo
Up vote any posts that you find helpful, it shows what's working..

Yes, This is a system requirement. We need flow control (but only for RTS pin).

So three differential pairs need to be run​

Tips, Buy me a coffee, or three.. PayPal Venmo
Up vote any posts that you find helpful, it shows what's working..

So, to work as full duplex, is it best to configure as rs232 (not rs485) with RTS ?

Depends on the application, you've indicated a desire to use differential drivers, to both transmit and receive simultaneously you will need at least two pairs.

Perhaps Google some images of RS-232, RS-485 and RS-422 interfaces so you have some conception about what's being discussed. ​

Tips, Buy me a coffee, or three.. PayPal Venmo
Up vote any posts that you find helpful, it shows what's working..

Do you mean pair of wires or of interfaces (ports) ?