Best Practice for ADC Reading & Op-Amp Toggling in Motor Control (STM32G431CBU6)

Raul_Posada
Associate II

Hello everyone,

I'd first like to mention that this project is being developed with support from ST Brasil, which has provided important components to aid in this development.

I'm working on firmware for motor control and, being new to this area, I'm looking for guidance on the best way to implement a specific part of the logic.

 

1. Summary and Context

 

Here is a summary of the hardware and MCU configuration:

  • Hardware: 3 low-side shunts. The signal from the Phase U shunt resistor is shared, acting as a common input for two of the MCU's integrated op-amps.

  • MCU Config:

1.1. Timer 1: Configured for Center-Aligned Mode 1. * CH1/CH1N, CH2/CH2N, CH3/CH3N are complementary PWM outputs. * CH4 is used to generate a capture-compare interrupt.

1.2. ARR Value: The ARR (Auto-Reload Register) value is 1000.

1.3. Interrupt Trigger: Timer 1 CH4 is set to generate a capture-compare interrupt when the CNT (counter) reaches 900.

1.4. Modulation Index: For modulation index purposes, the maximum value for CCR1, CCR2, and CCR3 should be 800.

1.5. Op-Amps: Configured for high-speed mode. The non-inverting input pin needs to be switched programmatically (in software).

1.6. ADCs: * Using DMA. * Regular conversions are triggered by software. * Scan Mode is On. * The "End of Sequence of conversions" (EOS) option is enabled.


 

2. My Main Question

 

(Thank you for reading this far.)

Given this configuration—specifically the need to read currents and switch the op-amp inputs—I'm trying to figure out the most robust and efficient way to handle the logic.

What is the best practice or recommended method for:

  1. Reading the ADC values?

  2. Saving the conversion data?

  3. Programmatically toggling the non-inverting inputs for the op-amps in sync with the PWM cycle?

  4. After the currents and voltages are read and saved, I will implement a state observer. Where in the execution flow (e.g., in which interrupt context, or in the main loop) should I perform these observer calculations to avoid race conditions with the data that is being updated by the DMA/ADC?

I'm looking for advice on the general approach .

Thank you for your time.

Best Regards,
Raul Undergraduate Student & Scientific Initiation
Universidade Federal de Santa Maria (UFSM)

1 REPLY 1
Ozone
Principal II

> 1. Reading the ADC values?
> 2. Saving the conversion data?

Both are closely related.
And assuming you want to implement a cycle-by-cycle control, you probably need one set of ADC input values (the configured channel sequence).

For that I would configure DMA for the number of bytes this sequence contains (two bytes per channel for 12-bit values) in single-burst mode, ADC-EOS as trigger (ADC configuration !), and enable the DMA-TC interrupt. This way, you get an interrupt whenever DMA has finished to transfer a sequence to your configured buffer.

When playing around with audio data, I used to configure DMA to a larger (integral) number of transfers.
But  since you probably want to feed the ADC values into the control algorithm cycle, this is not appropriate here.

> 3. Programmatically toggling the non-inverting inputs for the op-amps in sync with the PWM cycle?

I'm not really familiar with motor control, but probably a timer interrupt associated with the PWM generation.
I'm sure others here have more experience in this regard.

> 4. After the currents and voltages are read and saved, I will implement a state observer. Where in the execution flow (e.g., in which interrupt context, or in the main loop) should I perform these observer calculations to avoid race conditions with the data that is being updated by the DMA/ADC?

I personally would avoid the interrupt context here.
Refreshing my old electrical engineering subject stuff, an observer is basically a controller working on another controller instead of the controlled system itself.
I would run both in the main loop, usually the observer after the controller.
The trigger is a flag set in an interrupt - whichever signifies in your case that all data are gathered. Which might be said DMA-TC interrupt.