STEVAL-SPIN3202 Over Current Fault

  • July 20, 2020
  • 3 replies
  • 1014 views

Hi All,

Using a 36V motor that is rated for peak of 20.5A. I always get an overcurrent fault on startup even though my current output is only 0.8A. Any guidance would be appreciated, and I am happy to provide more details if needed.

Thanks,

-Nick

This topic has been closed for replies.
Best answer by Enrico Poli

Ok.

The comparator of the SPIN32F0A can be used in two different ways:

  1. OCP when connected to the BKIN input of TIM1
  2. Current control when connected to the ETR input of the TIM1

I guess you need case 1, so the proper hardware configuration in your case is Jumper 3 closed in 2-3 position:

0693W000003BGViQAO.png

In this way you will sense the voltage on the shunt directly instead of the amplified value.

If this is already your configuration, please share some of your waveforms.

3 replies

Enrico Poli
ST Employee
July 24, 2020

Hi Nick,

What is the contro algorithm? The STEVAL-SPIN3202 supports both FOC and 6STEP and the setup for the OCP changes according to the selected one.

Another question, what about the reference threshold of the comparator? STSPIN32F0A can select between different intervention values:

0693W000003BF6KQAW.png

Enrico

nmamore
nmamoreAuthor
Associate II
July 24, 2020

Hi Enrico,

I am attempting to use Hall Sensor control. I have tried all of the threshold values to no luck. I found that the signal that led into the comparator was very noisy and that seemed to be tripping the comparator.

Enrico Poli
Enrico PoliBest answer
ST Employee
July 24, 2020

Ok.

The comparator of the SPIN32F0A can be used in two different ways:

  1. OCP when connected to the BKIN input of TIM1
  2. Current control when connected to the ETR input of the TIM1

I guess you need case 1, so the proper hardware configuration in your case is Jumper 3 closed in 2-3 position:

0693W000003BGViQAO.png

In this way you will sense the voltage on the shunt directly instead of the amplified value.

If this is already your configuration, please share some of your waveforms.