First of all: VND5T100LAJ and VND5T100AJ differ essentially only in the package variants and in the values for current sensing. The switching times are completely identical, so you can expect the same achievable switching frequency.
Could it be that you want to reduce the power consumption of the relay with PWM?
If that is the case, then you should take a look at the datasheet for the HCX241CB, where under General Notes, point 4, it says:
Contactor has two coils. Both are used for pick-up, and then in approximately 75 milliseconds, one coil is electronically removed from the coil drive circuit. The remaining coil supplies low continuous hold power sufficient for the contactor to meet all of its specified performance specifications. This provides the lowest coil power possible without the use of PWM electronics that have been known to cause EMI emissions and/or cross-talk on your system control power.
Regardless of the purpose of PWM control: the maximum PWM frequency of 1...2kHz will result in an audible tone, which can only be avoided with frequencies above the audible range, but then increasingly causes EMI problems.